Hi folks
Some comments on this;
I would be cautious about assuming that people will be willing or able to
be transferred in an evac chair, or in a sling. The process of transferring
from their own wheelchair into these devices is uncomfortable, and
potentially dangerous for some people, depending on their disability. This
kind of transfer would normally be carried out by trained medical staff, so
you would need to ensure that any staff responsible for these transfers are
trained patient handling and manual handling. But even with that training,
don't assume that these devices will provide a solution for everybody.
There are also powered evacuation chair devices which will take a
wheelchair. The wheelchair user does not need to transfer out of their own
wheelchair to use these devices. Some of these can also travel upstairs,
which may be needed for basements. Big disadvantage is cost.
You may also want to consider using the existing lift, even without it
being upgraded to evacuation lift status. While we've all been drilled in
'Do not use the lift in case of emergency' for a generation, this is not an
absolute rule. Using a standard lift has risks attached, just as the
alternative methods of evacuation have risks attached. A risk assessment is
required to decide the best approach. The attached presentation from Derek
Smith of the UK's Lift and Escalator Industry Association (former technical
director of Otis Lifts UK) outlines the risks involved in this approach.
(See attached file: using lifts to escape DS UK.ppt)
Hope this helps
Shane
Shane Hogan
Project Manager - Excellence through Accessibility
National Disability Authority
Email: [log in to unmask]
Web: http://www.nda.ie/eta
Direct Line: 01-6080497
"Ryan, Justin"
<Justin.Ryan@SOUT
HEASTERNRAILWAY.C To
O.UK> [log in to unmask]
Sent by: cc
Accessibuilt list
<ACCESSIBUILT@JIS Subject
CMAIL.AC.UK> Re: Fire Evac
11/03/2010 16:53
Please respond to
Accessibuilt list
<ACCESSIBUILT@JIS
CMAIL.AC.UK>
Alan
Thanks for that it certainly looks to be a simpler and cheaper alternative
to an evac chair , I will discuss with the building management as cost is
as ever their biggest concern!
Kind Regards
Justin Ryan MSc MinstLM
Accessibility and Inclusion Manager
Southeastern,
Old Red Star Office
Canterbury East Station
Station Road East
Canterbury
Kent
CT1 2RB
F. 01233 617837
From: Accessibuilt list [mailto:[log in to unmask]] On Behalf Of
Hunt, Alan
Sent: 11 March 2010 16:50
To: [log in to unmask]
Subject: Re: Fire Evac
Hi again Justin
I don’t have any written evac plans but have been involved in assessing the
evacuation needs for individuals including involving their assistants,
parents, evacuation personnel etc. and advising on the best type of chair
(s) in specific circumstances. The main problem when the evacuee is
unknown though, such as in a public building, is whether the person is able
to transfer to an evacuation chair or not and in this regard we are
considering introducing “Promove” slings in conjunction with evacuation
chairs. These slings have been used by airlines to transfer individuals
from an aisle wheelchair to an aircraft seat and also at sports stadia to
evacuate casualties from difficult to reach areas between seating. The
sling is fairly easy to deploy and has handholds for up to (8? I think)
helpers. It is worth getting them along to give a demo because the sling
certainly appears to expand the possibilities and make evacuation chairs
more usable in more situations.
www.promove.uk.com
Regards
Alan Hunt
Access Officer
Pembrokeshire County Council
tel: 01437 775148
e-mail: [log in to unmask]
From: Accessibuilt list [mailto:[log in to unmask]] On Behalf Of
Ryan, Justin
Sent: 11 March 2010 16:22
To: [log in to unmask]
Subject: Re: Fire Evac
Thanks for all the information regarding an evacuation lift that I will
certainly be taking up with the building owners, but I would also like to
hear from anyone who has seen in place a good/robust fire evac plan
catering for and involving everyone especially where the use of alternative
evac methods are required i.e. evac chair etc.
Kind Regards
Justin Ryan MSc MinstLM
Accessibility and Inclusion Manager
Southeastern,
Old Red Star Office
Canterbury East Station
Station Road East
Canterbury
Kent
CT1 2RB
F. 01233 617837
From: Accessibuilt list [mailto:[log in to unmask]] On Behalf Of
Hunt, Alan
Sent: 11 March 2010 16:16
To: [log in to unmask]
Subject: Re: Fire Evac
Hi Jane
I was referring specifically to the upgrading of a passenger lift to an
evacuation lift as per BS9999 not the use of passenger lifts in emergency
situations as per the very useful document you posted.
Regards
Alan
Alan Hunt
Access Officer
Pembrokeshire County Council
tel: 01437 775148
e-mail: [log in to unmask]
From: Accessibuilt list [mailto:[log in to unmask]] On Behalf Of
Jane Simpson
Sent: 11 March 2010 13:44
To: [log in to unmask]
Subject: Re: Fire Evac
Not sure that it needs to be isolated at each level. My understanding is
that a risk assessment should be able to establish where the source of the
fire is, where is the power supply, is It likely to affect the lift on any
level? If not, then you can use it. If the fire is in another zone to the
lift, why would it require a protected lobby, the zone is the lobby.
Regards Jane
Jane Simpson
T: 01484 413000/537407
M: 07777 607239
www.janesimpsonaccess.com
(Embedded image moved to file: pic17110.jpg)
cid:image001.jpg@01C8A4BA.A15C1D20
Registered address: New House Bungalow, New House Road, Sheepridge,
Huddersfield, HD2 1EG Company No 6559802, VAT No 930 0839 42
This e-mail is for the addressee only. The information contained in it
and any attachments are confidential and may be privileged. If you have
received this e-mail in error, please notify us immediately. You are not
authorized to, and must not disclose, copy, distribute or retain this
e-mail or any part of it.
From: Accessibuilt list [mailto:[log in to unmask]] On Behalf Of
Hunt, Alan
Sent: 11 March 2010 11:50
To: [log in to unmask]
Subject: Re: Fire Evac
Justin
Not as such but as I understand it, it will need its own protected lobby at
each level to isolate it from the stair well to keep out smoke and fumes.
This is usually where the problems arise…. ie having sufficient space. For
info….. The new lift controls will disable the landing call buttons and
automatically return the lift it to the main exit level when the alarm is
activated. A responsible person then has to take control of the lift to
manage the evacuation, controlling the lift from within.
I ought to point out though that I am not an expert on evacuation lifts but
I have been involved in carrying out feasibilities to upgrade existing
lifts in our schools and other council buildings and have therefore carried
out a lot of research.
Alan
Alan Hunt
Access Officer
Pembrokeshire County Council
tel: 01437 775148
e-mail: [log in to unmask]
From: Accessibuilt list [mailto:[log in to unmask]] On Behalf Of
Ryan, Justin
Sent: 11 March 2010 11:07
To: [log in to unmask]
Subject: Re: Fire Evac
Alan
The building I have in mind where this is an issue has the normal 4 lifts
in a lobby but also has a 5th lift which is in a lobby next to the rear
fire evac stairs so this wouldn’t necessarily be that difficult – does this
mean it doesn’t necessarily need any extra fire proofing to the shaft ( I
am sure it is in a normal , enclosed concrete lift shaft) and that no
special smoke exhaust system etc needs to be present?
Thanks
Kind Regards
Justin Ryan MSc MinstLM
Accessibility and Inclusion Manager
Southeastern,
Old Red Star Office
Canterbury East Station
Station Road East
Canterbury
Kent
CT1 2RB
F. 01233 617837
From: Accessibuilt list [mailto:[log in to unmask]] On Behalf Of
Hunt, Alan
Sent: 11 March 2010 10:28
To: [log in to unmask]
Subject: Re: Fire Evac
Hi Justin
It is possible to upgrade passenger lifts to evacuation lift standard in
certain circumstances:
· The electronics in the lift and on the landings needs upgrading
and a communications system has to be installed…. this is usually fairly
simple to achieve.
· The lift must have a secondary, separate, independent power
supply – eg generator or separate main. This can usually be achieved.
· The lift must have a fireproof lobby, be associated with a
protected stairway and a have direct protected rout to exit. This can
prove difficult to achieve.
· The routes to the lift at each level will also need to be
looked at to make sure that safe travel distances can be achieved.
Regards
Alan
Alan Hunt
Access Officer
Pembrokeshire County Council
tel: 01437 775148
e-mail: [log in to unmask]
From: Accessibuilt list [mailto:[log in to unmask]] On Behalf Of
Jane Simpson
Sent: 11 March 2010 10:08
To: [log in to unmask]
Subject: Re: Fire Evac
**************************************************************************************************************
This document should only be read by those persons to whom it is addressed,
and be used by them for its intended purpose; and must not otherwise be
reproduced, copied, disseminated, disclosed, modified, distributed,
published or actioned. If you have received this email in error, please
notify us immediately by telephone on 01437 764551 and delete it from your
computer immediately. This email address must not be passed on to any third
party nor be used for any other purpose.
Pembrokeshire County Council Website - http://www.pembrokeshire.gov.uk
Please Note: Incoming and outgoing e-mail messages are routinely monitored
for compliance with our IT Security, and Email/Internet Policy.
This signature also confirms that this email message has been swept for the
presence of computer viruses and malicious code.
***************************************************************************************************************
Dim ond y sawl y mae'r ddogfen hon wedi'i chyfeirio atynt ddylai ei
darllen, a'i defnyddio ganddynt ar gyfer ei dibenion bwriadedig; ac ni
ddylid fel arall ei hatgynhyrchu, copio, lledaenu, datgelu, addasu,
dosbarthu, cyhoeddi na'i rhoi ar waith chwaith. Os ydych chi wedi derbyn yr
e-bost hwn trwy gamgymeriad, byddwch cystal a rhoi gwybod i ni ar unwaith
trwy ffonio 01437 764551 a'i ddileu oddi ar eich cyfrifiadur ar unwaith. Ni
ddylid rhoi'r cyfeiriad e-bost i unrhyw drydydd parti na'i ddefnyddio ar
gyfer unrhyw ddiben arall chwaith.
Gwefan Cyngor Sir Penfro - http://www.pembrokeshire.gov.uk
Sylwer: Mae negeseuon e-bost sy’n cael eu hanfon a’u derbyn yn cael eu
monitro’n rheolaidd ar gyfer cydymffurfio ⦣8217;n Diogelwch TG, a’n Polisi
E-bost/Rhyngrwyd.
Mae'r llofnod hwn hefyd yn cadarnhau bod y neges e-bost hon wedi cael ei
harchwilio am fodolaeth firysau cyfrifiadurol a chod maleisus.
***************************************************************************************************************
Southeastern is a wholly owned subsidiary of Govia Ltd, which is part of
The Go-Ahead Group plc and Keolis. The information herein, including any
transmitted files, is confidential; intended for the addressee only; and
contains only the personal views of the author. The Go-Ahead Group plc and
its subsidiaries shall not be bound by anything herein and shall not be
liable for any losses as a result of virus transmission, although
endeavours are made to protect against this. If you have received this
e-mail in error please notify the originator.
Southeastern (is a trading name of London & South Eastern Railway Ltd) is
registered in England No. 04860660, The Go-Ahead Group plc is registered in
England No. 2100855 and Govia is registered in England No. 3278419).
The Registered Office: 3rd Floor, 41-51 Grey Street, Newcastle-upon-Tyne
NE1 6EE
P Please consider the environment before printing this e-mail
----------End of Message---------- Run by SURFACE for more information on
research, consultancy and the distance taught MSc. in Accessibility and
Inclusive Design programme visit: http://www.surface.salford.ac.uk Archives
for the Accessibuilt discussion list are located at
http://www.jiscmail.ac.uk/lists/accessibuilt.html
----------End of Message---------- Run by SURFACE for more information on
research, consultancy and ----------End of Message---------- Run by SURFACE
for more information on research, consultancy and the distance taught MSc.
in Accessibility and Inclusive Design programme visit:
http://www.surface.salford.ac.uk Archives for the Accessibuilt discussion
list are located at http://www.jiscmail.ac.uk/lists/accessibuilt.html
Southeastern is a wholly owned subsidiary of Govia Ltd, which is part of
The Go-Ahead Group plc and Keolis. The information herein, including any
transmitted files, is confidential; intended for the addressee only; and
contains only the personal views of the author. The Go-Ahead Group plc and
its subsidiaries shall not be bound by anything herein and shall not be
liable for any losses as a result of virus transmission, although
endeavours are made to protect against this. If you have received this
e-mail in error please notify the originator.
Southeastern (is a trading name of London & South Eastern Railway Ltd) is
registered in England No. 04860660, The Go-Ahead Group plc is registered in
England No. 2100855 and Govia is registered in England No. 3278419).
The Registered Office: 3rd Floor, 41-51 Grey Street, Newcastle-upon-Tyne
NE1 6EE
P Please consider the environment before printing this e-mail
**********************************************************************************
The information transmitted is intended only for the person or entity to which it is addressed and may contain confidential and/or privileged material. Any review, retransmission, dissemination or other use of, or taking of any action in reliance upon, this information by persons or entities other than the intended recipient is prohibited. If you received this in error, please contact the sender and delete the material from any computer. It is the policy of the Department of Justice, Equality and Law Reform and the Agencies and Offices using its IT services to disallow the sending of offensive material.
Should you consider that the material contained in this message is offensive you should contact the sender immediately and also mailminder[at]justice.ie.
Is le haghaidh an duine nó an eintitis ar a bhfuil sí dírithe, agus le haghaidh an duine nó an eintitis sin amháin, a bheartaítear an fhaisnéis a tarchuireadh agus féadfaidh sé go bhfuil ábhar faoi rún agus/nó faoi phribhléid inti. Toirmisctear aon athbhreithniú, atarchur nó leathadh a dhéanamh ar an bhfaisnéis seo, aon úsáid eile a bhaint aisti nó aon ghníomh a dhéanamh ar a hiontaoibh, ag daoine nó ag eintitis seachas an faighteoir beartaithe. Má fuair tú é seo trí dhearmad, téigh i dteagmháil leis an seoltóir, le do thoil, agus scrios an t-ábhar as aon ríomhaire. Is é beartas na Roinne Dlí agus Cirt, Comhionannais agus Athchóirithe Dlí, agus na nOifígí agus na nGníomhaireachtaí a úsáideann seirbhísí TF na Roinne, seoladh ábhair cholúil a dhícheadú.
Más rud é go measann tú gur ábhar colúil atá san ábhar atá sa teachtaireacht seo is ceart duit dul i dteagmháil leis an seoltóir láithreach agus le mailminder[ag]justice.ie chomh maith.
***********************************************************************************
|